I am an engineer with a client in the frozen food business. A manufacturer of their freezer boxes is modifying condensing units from Copeland by adding a Compressor Rack Optimizer (CRO) which throttle the refrigerant flow through the suction line to limit compressor loading.
The Copeland nameplate lists the minimum circuit ampacity as 36.0 and maximum fuse size as 60, but the freezer box manufacturer is wiring the boxes with 30 ampere cords and connectors. The freezer box manufacturer states that we only need to provide a 30 amp branch circuit for each truck.
I am trying to comply with NEC Article 440 and obey Copeland's nameplate. NEC Article 440 does not reference the use of CROs.
Must I comply with the condensing unit nameplate, or may I disregard the nameplate and trust that the CRO will prevent an electrical overload?