I want to install a two gang 100 amp meter base with disconnects for each can I run the feeder wires in the same conduit in to the building ? what code article ?
I want to install a two gang 100 amp meter base with disconnects for each can I run the feeder wires in the same conduit in to the building ? what code article ?
If the disconnects are outside with the meters, then the downstream circuits are feeders, not services. You just have to remember to derate for multiple current-carrying conductors.