GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
I think that they are implying that the interior disconnects in each unit are in fact the service disconnects and what we have is several services feeding one building rather than one service entrance with multiple service conductor sets.
I have not compared that area of [2014] to [2011].
 