If the equipment is old and lacks a proper data plate, then a rule of thumb is to allow one KVA per horsepower, for motor losses and imperfect power factor.
So 20 HP may be assumed to be about 20KVA.
If one also allows for a 240 volt nominal service being actually 230 volts at the motor, then that gives a running current of 87 amps.
If one allows for the actual voltage being 220, which is likely with a service on the low side and a long feeder or branch circuit, then the running current would be about 91 amps.