HarryHomeowner
Member
- Location
- Baltimore, Maryland USA
Hi All - thanks in advance for any light you can shed on this issue.
I have a customer who wants me to install a TVSS receptacle (Hubbell 5360SA) in his basement that will serve computer equipment (routers, switches, modems, etc.). The receptacle needs to be mounted in a location that's about 10 feet away from the panel. The manual for this receptacle clearly states:
"CAUTION: Do not install this device if there is not at least 10 meters (30 feet) or more of wire between the electrical outlet and the electrical service panel."
In my situation, there will only be 10 feet, not 30. I called Hubbell and they referred me back to NEC 285.25, which states this requirement for all Type 3 SPD (I think SPD is Surge Protection Device). Apparently the code was recently revised to state that only Type 3 SPDs which specifically state the requirement for being installed at least 10 meters / 30 feet must actually be installed that way -- so if the manufacturer doesn't state this requirement for their Type 3 SPD, then the installer doesn't have to follow the requirement. But since this Hubbell receptacle (and other similar TVSS receptacles I've looked at) all do seem to have this requirement, I'm stuck.
QUESTION- What is the intent behind requirement? What could go wrong if the receptacle is installed closer than 30' to the panel? I asked the Hubbell support person this question, and they started to get very nervous because I was "asking them how to deliberately go around NEC code" -- not true. I just want to know why this is considered dangerous.
Thanks!
-Brian
I have a customer who wants me to install a TVSS receptacle (Hubbell 5360SA) in his basement that will serve computer equipment (routers, switches, modems, etc.). The receptacle needs to be mounted in a location that's about 10 feet away from the panel. The manual for this receptacle clearly states:
"CAUTION: Do not install this device if there is not at least 10 meters (30 feet) or more of wire between the electrical outlet and the electrical service panel."
In my situation, there will only be 10 feet, not 30. I called Hubbell and they referred me back to NEC 285.25, which states this requirement for all Type 3 SPD (I think SPD is Surge Protection Device). Apparently the code was recently revised to state that only Type 3 SPDs which specifically state the requirement for being installed at least 10 meters / 30 feet must actually be installed that way -- so if the manufacturer doesn't state this requirement for their Type 3 SPD, then the installer doesn't have to follow the requirement. But since this Hubbell receptacle (and other similar TVSS receptacles I've looked at) all do seem to have this requirement, I'm stuck.
QUESTION- What is the intent behind requirement? What could go wrong if the receptacle is installed closer than 30' to the panel? I asked the Hubbell support person this question, and they started to get very nervous because I was "asking them how to deliberately go around NEC code" -- not true. I just want to know why this is considered dangerous.
Thanks!
-Brian