25kVA Transformer secondary

Status
Not open for further replies.
I am using a 25kva encapsulated transformer (480V-240/120V) feeding two Nema 7 panelboards. Can I use a lug (with the two separate wires) inside the transformer wiring vault to feed both panelboards? I have primary protection and both the panelboards will have the secondary protection for the transformer. I was told I couldn't use the transformer like a junction box. I didn't really think it would be considered using it as a junction box. I can add a secondary enclosure with distribution blocks to do this but didn't want to add more enclosures to the already crowded switch rack.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I know of no Code section that prohibits such as long as the lug is properly rated and see it done often albeit usually on larger transformers.
 