Uni-strut Mounted Electrical Equipment

Status
Not open for further replies.

Shujinko

Senior Member
Looking to mount some electrical equipment (panels, small xfmr) outside on a uni-strut structure. Is there any code that requires me to get structural loading calculations to make sure the uni-strut structure will hold the weight of the electrical equipment?

BTW, I am in Florida. So FBC does apply. Thanks.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
I'm sure it does but I have never checked. Does anybody? I think of it like 2x4 lumber; just use it when it fits the need.

Download their design manual, it has all you need and more about what loads various elements can handle. For the basic P1000 strut, it can handle a maximum uniform load at 36" of 1130 lbs. for a single member.
 

mgookin

Senior Member
Location
Fort Myers, FL
Looking to mount some electrical equipment (panels, small xfmr) outside on a uni-strut structure. Is there any code that requires me to get structural loading calculations to make sure the uni-strut structure will hold the weight of the electrical equipment?

BTW, I am in Florida. So FBC does apply. Thanks.

Yes, technically speaking. It's up to the bldg dept where you are doing the work to dictate what level of detail you need. Give them a call, ask for the electrical plans examiner, and tell them how much equipment it is, etc. and ask how much detail they need on structural drawings & if it needs to be signed by a PE for structural.
 

Shujinko

Senior Member
Thanks for the great responses. I will def look at the uni-strut design manual and try to coordinate with the AHJ on this. Thanks again!
 