Wye Distribution to Delta Transformer

Status
Not open for further replies.

Target1

Member
Location
United States
You can connect a delta to wye transformer (delta prim 12470 / wye secondary 480/277) to a wye distribution system correct? Distribution is at 12470...

Thanks!
 
Last edited:

Target1

Member
Location
United States
No, I am doing:

WYE 12470 (distribution from the pole from utility) and connecting it to a 12470Delta / 480(277Y) transformer to connect as a wye to wye switchgear and then serves wye loads.

This is a typical connection, correct?


Edit1: I am just trying to make sure it is ok to connect a delta to wye transformer to a wye source ?

Thanks
 

ron

Senior Member
I misunderstood your topology.

I will guess that the 12470V wye will be N-G bonded upstream somewhere at the service.

Then you situation will be fine / typical. Bond the N-G again at the secondary of your D-Y transformer
 