Calculated Single phase loads with 3 phase panel

Status
Not open for further replies.

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
This has been discussed in a closed thread. I have a question. The load calculated out as Phase A= 416, B=375 and C= 375. According to Charlie's post we should add all 3 loads and divide by 3 and we get 388 amps. Why would we not use the highest load. In theory if we installed a 400 amp breaker isn't phase by going to cause a problem.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
I agree.
If you are only going to use the amp value in a upstream KVA calculation of single core transformer size, then using 388 makes some sense.
But for the purpose of sizing conductors and OCPD, you need to use the larger value.

Tapatalk!
 

kwired

Electron manager
Location
NE Nebraska
I read charlies post as saying the 388 amps is the average for all three phases, which I agree with. It doesn't tell us individual load on each phase. One could throw the balance off even further by changing connection of some heaters to different phases and you would still have a 388 average.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Well it was interesting because the value the OP got was 388 even with rounding off. I guess I was confused and thought they were saying 388 is the size-- didn't make sense that is why I asked.
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
This has been discussed in a closed thread. I have a question. The load calculated out as Phase A= 416, B=375 and C= 375. According to Charlie's post we should add all 3 loads and divide by 3 and we get 388 amps. Why would we not use the highest load. In theory if we installed a 400 amp breaker isn't phase by going to cause a problem.

388 Amps is average. Not sure what that gets you, or is even useful. I have never used average amps for a 3 phase panel before.

Everything on a panel for sizing should be based on first determining KVA, (individual branch, phase, and total) then calculating the amps.

Now, your question, yes, if you used the information above, the breaker would need to be based on the 416A.
 