ASG
- Work in NYC
- Electrical Engineer, PE
Is there anywhere in the code that says that you should or even can put the HVAC serving an Emergency Room on the Equipment Emergency branch?
It's allowed in 517.34. In my area a lot of the HVAC equipment will be fed from 1 or more equipment ATS.
I doesn't appear to be listed in A or B. A only mentions supply, return and exhaust systems for operating and delivery rooms.
Supply, return and exhaust...wouldn't that be HVAC?
Yes but Emergency Room is not the same as Operating and Delivery Rooms....
Tapatalk!