a heat exchanger is being installed in a small rm 5x5 it requires a 30 amp 220 volt disconnect . does this disconnect does this disconnect have to meet the requirements of table 110 .26 a 1 which states condition 1 and requires 3 ft what if the requirement cant be met can the disconnect be mounted on the out side wall of the enclosure which has the space required by 110. 26 ( a) (1)
 

ASG

Senior Member
Location
Work in NYC
Occupation
Electrical Engineer, PE
a heat exchanger is being installed in a small rm 5x5 it requires a 30 amp 220 volt disconnect . does this disconnect does this disconnect have to meet the requirements of table 110 .26 a 1 which states condition 1 and requires 3 ft what if the requirement cant be met can the disconnect be mounted on the out side wall of the enclosure which has the space required by 110. 26 ( a) (1)

I would think it would be a supplemental disconnect and would fall under 240.10.
 

mgookin

Senior Member
Location
Fort Myers, FL
a heat exchanger is being installed in a small rm 5x5 it requires a 30 amp 220 volt disconnect . does this disconnect does this disconnect have to meet the requirements of table 110 .26 a 1 which states condition 1 and requires 3 ft what if the requirement cant be met can the disconnect be mounted on the out side wall of the enclosure which has the space required by 110. 26 ( a) (1)

Do we have a room and an enclosure?
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
a heat exchanger is being installed in a small rm 5x5 it requires a 30 amp 220 volt disconnect . does this disconnect does this disconnect have to meet the requirements of table 110 .26 a 1 which states condition 1 and requires 3 ft what if the requirement cant be met can the disconnect be mounted on the out side wall of the enclosure which has the space required by 110. 26 ( a) (1)

110.26 does not apply. You are not working the disconnect 'hot'. Treat it like you would for a disconnect for a furnace.

I would think it would be a supplemental disconnect and would fall under 240.10.

240.10 Supplementary Overcurrent Protection.
 

mwm1752

Senior Member
Location
Aspen, Colo
a heat exchanger is being installed in a small rm 5x5 it requires a 30 amp 220 volt disconnect . does this disconnect does this disconnect have to meet the requirements of table 110 .26 a 1 which states condition 1 and requires 3 ft what if the requirement cant be met can the disconnect be mounted on the out side wall of the enclosure which has the space required by 110. 26 ( a) (1)

Is this a fusible disconnect? Is there ready access to the overcurrent device to shut down power?
 