I am a little confused about 445.13. It states that "The ampacity of the conductors from the generator to the first distribution device containing over current protection shall not be less than 115% of the nameplate rating of the generator.
I thought that this referred to the wiring from the actual generator lugs to the first breaker, which often is right on the generator. A recent discussion with an inspector is telling me otherwise. Basically saying that the load wires on a generator must be 115% of the generator nameplate rating. This doesn't make sense to me since they are protected by the 125A circuit breaker on the distribution side of the generator. Can someone tell me the reason for this code? Is seems to me that if the load wires are protected by a 125A breaker then the wire should need to be rated for 125 amps.
Also as a bonus question 310.15(b)6 allows 120/240 residential service and feeder to use the 310.15(b)6 table for ampacity. does this apply to the generator conductors as well if they are supplying the service to a residence?
I thought that this referred to the wiring from the actual generator lugs to the first breaker, which often is right on the generator. A recent discussion with an inspector is telling me otherwise. Basically saying that the load wires on a generator must be 115% of the generator nameplate rating. This doesn't make sense to me since they are protected by the 125A circuit breaker on the distribution side of the generator. Can someone tell me the reason for this code? Is seems to me that if the load wires are protected by a 125A breaker then the wire should need to be rated for 125 amps.
Also as a bonus question 310.15(b)6 allows 120/240 residential service and feeder to use the 310.15(b)6 table for ampacity. does this apply to the generator conductors as well if they are supplying the service to a residence?