Circuits for LED pole mounted fixtures

Status
Not open for further replies.

olc

Senior Member
Quick question:
Can typical pole mounted LED area light fixtures (say for parking) be protected with a 30A circuit breaker? (as opposed to a 20A)
 

Smart $

Esteemed Member
Location
Ohio
The lighting units would have to meet the heavy-duty lampholder requirement of 210.23(B) in other than dwellings.
 