680.21 (4) In the interior of a residence NM cable is permitted, now if I was coming out of a interior sub panel to supply pool, then that sub panel would have to be installed with an insulated ground contained in PVC or similar method. 680.25? I'm I understanding this correctly or over thinking it?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If you are feeding pool branch circuits from an existing sub-panel, there is an exception in 680.25(A)(1) that permits the feeder to that sub-panel to have an equipment grounding conductor in the cable assembly (with stipulations).
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
If you are feeding pool branch circuits from an existing sub-panel, there is an exception in 680.25(A)(1) that permits the feeder to that sub-panel to have an equipment grounding conductor in the cable assembly (with stipulations).


Taken literally this only allows the existing feeder to be in a cable assembly. It does not appear to include the feeder to a pool panel. IMO, that feeder from the existing sub panel cannot be in a cable assembly. ????
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I agree thus my mention of "existing" and "branch circuits".
I was really not clear if the "pool subpanel" the OP mentioned is the original subpanel or an added one. I should have been more specific and appreciate your additional post.
 

fjm

Member
Location
NJ
Thanks, so to clarify a new sub panel for pool branch circuits would be required to be feed with insulated ground regardless of that panel being indoor residence.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Yes. Insulated ground in a conduit meting the requirement per 680.25
 