electrofelon
- Cherry Valley NY, Seattle, WA
when, if ever, would you connect the neutral of a wye system to the primary along with the ungrounded conductors?
Your question is extremely vague. There must be a reason for your question.when, if ever, would you connect the neutral of a wye system to the primary along with the ungrounded conductors?
Just a general question. I just cant think of when it would be necessary or what it would accomplish, and there have been multiple threads on here recently when the consensus was to leave it off.....So wye land it ?
There are times that you do but the OP has neglected to provide any information about the application and as such there are times that you don't.
To provide a answered as you have done may be a correct answer but it is based upon an assumption.
I restate my original reply:I dont quite understand your response. Perhaps you didnt notice I was the original poster and responding to you not the OP?
My previous reply was cut off at the bottom and as such this is a resend:I restate my original reply:
"Your question is extremely vague. There must be a reason for your question.
Is this a test question or is it simply curiosity? I can think of one very common application that could be answered in one simple reply but there are also other less common applications also."
OK, well start with the question and answer routine as it is difficult to provide a diffinitive answer while being provided very limited information.
Is your question in regards to a POCO substation or other power distribution transformer where a wye primarary is commonly used or may I venture to guess that you are referring to a 480d-208y/120 transformer being used to step up from 208v 3ph- 480v 3ph.
Often people ask questions in a way to get an answer that they want wa
Most awesome, Thanks. What you have described so well is an application that most are not familiar with.This is commonly done by utilites on underground distribution systems to prevent ferroesonance when the supply switches can be operated one pole at a time. See IEEE Std 142-2007 starting on about page 30 if you have access.
I would be enclined to "assume" that he may be referring to using a common 480v delta to 208y/120 step down transformer as a step up transformer but I'm reluctant to answer based upon my assumption.
Unless the OP can define his application it would be irresponsible for us to submit a reply based upon guessing what he means. It's similar to pulling teeth.
I am trying to understand exactly what you are asking.when, if ever, would you connect the neutral of a wye system to the primary along with the ungrounded conductors?
If you connect all those points together you have a pretty good fault current, or else I am not understanding what you are talking about. You could do so beyond an open switch as extra safety should the switch get closed for some reason when doing work on the lines.
This is the problem with vague question. If the question was specific then the answer can be provided directly for that question. If it is vague either a reference book or resource can be given so that the OP can take the time read about the "subject" them selves. You may notice that when a question is vague and not specifics it generated a lot AF answers based upon assumptions, guesses, "I think that what he means" which can be misunderstood by the OP otherwise he would have been more specific with his questionI think he is just asking when should you use the primary neutral on a Wye-wye or Wye-delta transformer & what is the problem if you should connect the neutral & do not.
From my perspective I would venture to " guess" that he may be referring to a delta/wye step down transformer that is intended to be used as a step up transformer where you are feeding the wye. If the supply is a 208y/120 and you have L1-L2-L3,N,G and the transformer's X1,X2,X3,X0 how do you connect them. I have found that it was not all that unusual for the primary of a transformer to order with a wye primary based upon their supply being a 208y/120. Yes, it happens.
I have to explain that when using a 480d-208y/120 as a step I instruct them to just bring out the 208 L-L-L and EGC conductors only, no need for the neutral. Make sure that the X0 of the transformer is unbounded from the transformer enclosure leaving the X0 floating, simply terminating the lines to the X connection on the transformer and the EGC to the frame/enclosure of the transformer.
But that is simple. What has been avoided if my scenario is true what do you do with a 480v delta secondary? Are they familiar with ungraunded/grounded/ground detection, etc? Feeding a wye primary is simpler to address that the understanding of what to do whith a Delta secondary.
Is this the actual application that the OP may be referring to?
Thanks for following up.Yes that is one scenario, although just a little more specific. Perhaps a better rewording of the original question would be "given a transformer with a wye primary and a wye system supply, are there situations when you do or don't connect the primary neutral to the primary xo? If so what?"
Templdl from your scenario, what happens if the neutral is connected? Does the answer change if the secondary is left ungrounded vs corner grounded?