I am currently feeding a 1600 amp switchgear from a transformer that will require (5) sets of 600kcmil conductors. Due to spacing issues we have decided to utilize a wireway/trough in lieu of individual flex raceways. I have sized the wireway as a 10x10 but would like some feedback as to what sections of the code I need to review to ensure I have sized the wireway correctly given the (2) 600kcmil conductors that will pass through the wireway from the transformer to the switchgear. Any feed back would be appreciated. I only get one shot at getting this right! Thanks!
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
(In regard to your post referencing this "lost posting". New posts are held for review to reduce the change of spam, etc.)
Welcome to the Forum. No doubt your question will be addressed shortly.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Assuming a metal wireway, Art 376.22 addresses fill.
You mentioned (5) sets of 600 kcmil then later, (2) sets. Can you clarify what conductors will be in the wireway ?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Are we talking a 10" x 10" I hope not, or 10'x10'. Is this truly a wireway or JB. How deep?

good question. how in the heck do you have enough bending space with a 10" raceway and 20 600MCM wires? you might get them all in the wireway if they all came in one end and went out the other and there was no entry through the sides.
 
Last edited:
The only derating that has to be factored (I think) is if you have more than (30) current carrying conductors in a wireway. Basically, I have to feed a piece of switchgear and it would be more effective to install a wireway between the transformer and the switchgear in lieu of (5) 4" flexible metal conduits. I am looking for the correct size wireway to install to make the installation code compliant.
 
The wireway would be installed between the transformer and the switchgear. There is only about 18" between the two. Rather than having (5) 4" flexes, I wanted to install a wireway as a means of feeding the switchgear. It is basically like a nipple, but I would be using a wireway instead of emt or grc. I cannot figure out how big the wireway would need to be to comply with the NEC.
 

Smart $

Esteemed Member
Location
Ohio
The wireway would be installed between the transformer and the switchgear. There is only about 18" between the two. Rather than having (5) 4" flexes, I wanted to install a wireway as a means of feeding the switchgear. It is basically like a nipple, but I would be using a wireway instead of emt or grc. I cannot figure out how big the wireway would need to be to comply with the NEC.
Assuming 20 THHN (no reduced neutral?) ? 0.8676 in?/conductor = 17.352in?

Assuming a supply side bonding jumper, 5 ? 600kcmil ? 12.5% = 375kcmils, rounded up to 400kcmil = 0.416in?

17.352in? + 0.416in? = 17.768in?

17.768in? ? 20% maximum fill = 88.84in? minimum cross sectional area.

10"?10" wireway at 100in? is compliant.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
It is interesting to me that a jb would need to be much larger than a wireway. I wonder why. They are basically the same space wise.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
It is interesting to me that a jb would need to be much larger than a wireway. I wonder why. They are basically the same space wise.
Possibility:

The JB calculation assumes that the wires will be coming in through limited openings (i.e. knockouts, etc.) while the raceway calculation assumes that the wires will come in anywhere in the open end cross section. That means all of the square cross section space is available, not just a bunch of circular cross sections within the square, which can waste space. And there would be fewer problems making the bends, etc. to enter into and exit the wireway.
JMSWAG.
 

Smart $

Esteemed Member
Location
Ohio
Possibility:

The JB calculation assumes that the wires will be coming in through limited openings (i.e. knockouts, etc.) while the raceway calculation assumes that the wires will come in anywhere in the open end cross section. That means all of the square cross section space is available, not just a bunch of circular cross sections within the square, which can waste space. And there would be fewer problems making the bends, etc. to enter into and exit the wireway.
JMSWAG.
In short, the wireway is used strictly as a wireway and not as a pull/junction box.
 