Well off the main 1200 disconnect there are two taps. One tap feeds a four motor branch circuit. Then the other tap feeds a single motor soft start. The branch circuit tap is sized correctly. The other tap is feed with the same size wire as the secondary out of the soft start. Is the single tap OK because it doesn't feed but one motor?
Can we straighten out one thing here and try to get the terminology straight?:
You have a 1200 amp main disconnect, and then on the load side of that disconnect, without any individual OCPD, you have two sets of wires going other places, and neither set of wires has a rated ampacity of 1200 amps or more?
If that is the case, then you probably have two taps, yes.
If the single motor and its soft start together have some sort of internal OCPD which properly protects the wire going to it, then depending on length and actual ampacity of the wire you may have a legal tap. The 1200A breaker in the soft start alone will not do this if the wire is rated for only 600A. But if the motor itself has an internal overload at 600A, then you may be OK.
If the four motor "branch" circuit (probably a feeder) has a single OCPD (which is what makes it a branch circuit) then, again depending on the length and the wire ampacity compares to the rating of that OCPD, then you may have a legal tap.
Whether the conductors, disconnects and OCPD within that multi-motor branch circuit (if that is what it is, rather than a feeder and several branches!) are really correct or not gets complicated.
You have not told us the size of any of the conductors (except the 600mcm??).