I understand the transliteration of this code.
I understand the inverter is actually pushing power into the main buss bars.
The utility (thru the main OCPD) *is also pushing power into the main buss bars.
Is the reason that we don?t go over this amount due to the fact that the main buss bars (only rated up to 120 percent) *would be put at risk due to the 2 sources of power pushing into the main buss bar and over-rating *it more than 120%?
*
I guess this makes sense, I just don?t ever see this happening. *Loads are created on demand, not on supply right? I?m just curious on your take on this. On the other hand, If you were to compare this to AIC ratings from a transformer, then were talking about potential, and that makes sense. Also I guess if there was a short downstream (between these 2 feeds) and both OCPD?s did not work, then this 120% rule would really come into play.
*
I understand the inverter is actually pushing power into the main buss bars.
The utility (thru the main OCPD) *is also pushing power into the main buss bars.
Is the reason that we don?t go over this amount due to the fact that the main buss bars (only rated up to 120 percent) *would be put at risk due to the 2 sources of power pushing into the main buss bar and over-rating *it more than 120%?
*
I guess this makes sense, I just don?t ever see this happening. *Loads are created on demand, not on supply right? I?m just curious on your take on this. On the other hand, If you were to compare this to AIC ratings from a transformer, then were talking about potential, and that makes sense. Also I guess if there was a short downstream (between these 2 feeds) and both OCPD?s did not work, then this 120% rule would really come into play.
*