Unfinished basement, laundry area, HVAC receptacle

Status
Not open for further replies.

mek421

Member
Location
Upstate NY, USA
Under current NY residential code, may a receptacle in the laundry area, on the laundry circuit, satisfy the E3801.11 receptacle outlet requirement for servicing of HVAC equipment, assuming the receptacle is sufficiently close to the furnace?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Under the NEC any accessible 120 volt receptacle on the same level would satisfy the requirement as long it's within 25'. Not sure about the NY res code.
 