How is the KVA of a single phase transformer calculated if the load is a mix 240V and 120V circuits? Assume the phases have a balanced load and the loads are either all on or all off.
How is the KVA of a single phase transformer calculated if the load is a mix 240V and 120V circuits? Assume the phases have a balanced load and the loads are either all on or all off.
KVA is still KVA. If both 120 coils are balanced you are ok. You can not load one side to more than half the KVA rating of the transformer. Where there is trouble is if there is unbalanced current and one side should happen to have more than half the KVA rating of the transformer connected to it.How is the KVA of a single phase transformer calculated if the load is a mix 240V and 120V circuits? Assume the phases have a balanced load and the loads are either all on or all off.
Add up the currents drawn by all the 240 volt loads, and multiply that number by 240. Add up the currents drawn by all the 120 volt loads, and multiply that number by 120. Add the two values together to get the total KVA on the transformer. Is that what you were asking for?How is the KVA of a single phase transformer calculated . . . ?
You're welcome. Also welcome to the forum. I think you will like the information that bounces around here."KVA is still KVA" cleared my confusion. I am helping to wire oil processing machinery that is mounted inside trucks .The installation uses a mix of 480V,240V and 110V. Since space ,weight and ,of course, cost are important I needed to check that the single phase transformers used are just right. Thanks for the help.