What spacing must be maintained when working with nonmetallic sheathed cable?

Status
Not open for further replies.

Tester101

Member
Location
New York
Code:
[B]334.80 Ampacity[/B] ... Where more than two NM cables containing two or more current-carrying conductors are installed, without [I][B]maintaining spacing[/B][/I] between the cables, through the same opening in wood framing that is to be fire- or draft-stopped using thermal insulation, caulk, or sealing foam, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(B)(2)(a) and the provisions of 310.15(A)(2), Exception, shall not apply. 
Where more than two NM cables containing two or more current-carrying conductors are installed in contact with thermal insulation without [I][B]maintaining spacing[/B][/I] between cables, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(B)(2)(a).

Where is the spacing between cables that must be maintained defined?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
That is a question that has no answer. The code says to maintain spacing without a clue to distance. IMO that means as long as the cables don't touch then the spacing requirement is satisfied
 

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
In the same place that defines what is subject to physical damage.

Its in the inspectors head. Hopefully your local inspection department has some guidelines so all inspectors in a locality use the same judgement criteria. I hate it when inspectors A says to do this and then inspector B says that's not good enough.
 

Gregg Harris

Senior Member
Location
Virginia
Occupation
Electrical,HVAC, Technical Trainer
Code:
[B]334.80 Ampacity[/B] ... Where more than two NM cables containing two or more current-carrying conductors are installed, without [I][B]maintaining spacing[/B][/I] between the cables, through the same opening in wood framing that is to be fire- or draft-stopped using thermal insulation, caulk, or sealing foam, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(B)(2)(a) and the provisions of 310.15(A)(2), Exception, shall not apply. 
Where more than two NM cables containing two or more current-carrying conductors are installed in contact with thermal insulation without [I][B]maintaining spacing[/B][/I] between cables, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(B)(2)(a).

Where is the spacing between cables that must be maintained defined?

Do you have a specific situation you are asking about? You are in the right section.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Do you have a specific situation you are asking about? You are in the right section.
As far as I know, there is nothing in the NEC that defines "spacing". There are rules that require you to have spacing, but no direction as to how big of a gap equals spacing.
 

Gregg Harris

Senior Member
Location
Virginia
Occupation
Electrical,HVAC, Technical Trainer
As far as I know, there is nothing in the NEC that defines "spacing". There are rules that require you to have spacing, but no direction as to how big of a gap equals spacing.

True nothing specific on the spacing. But the calculation for bundling may apply for the OP.
there may be a 2 inch hole with 15 home runs feeding to the panel.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
True nothing specific on the spacing. But the calculation for bundling may apply for the OP.
there may be a 2 inch hole with 15 home runs feeding to the panel.
Yes it might apply, but since we don't know what spacing is required we don't know if that rule applies.
 