Electrical room size..

Status
Not open for further replies.

Murrin67

New member
Location
Quincy, Ma. USA
Looking into installing a 1200amp main in an old piece of property.. I can't seem to find definitive space requirements in the book.. It is a commercial space so for starers, does the electric room require 2 forms of access and egress??
 

HoosierSparky

Senior Plans Examiner, MEP
Location
Scottsdale AZ
Occupation
Senior Plans Examiner
Size matters!

Size matters!

Looking into installing a 1200amp main in an old piece of property.. I can't seem to find definitive space requirements in the book.. It is a commercial space so for starers, does the electric room require 2 forms of access and egress??

Look at 110.26 (C) (1-3).:cool:
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
It is not the room that would, or would not, require two paths for egress. It is the working space that has that requirement.
 

Gregg Harris

Senior Member
Location
Virginia
Occupation
Electrical,HVAC, Technical Trainer
110.26(3)

(C)
Entrance to and Egress from Working Space. (1) Minimum Required. At least one entrance of sufficient area shall be provided to give access to and egress from working space about electrical equipment.

The requirements in this section are intended to provide access to electrical equipment. However, the primary intent is to provide egress from the area so that workers can escape if there is an arc-flash incident.


(2) Large Equipment. For equipment rated 1200 amperes or more and over 1.8 m (6 ft) wide that contains overcurrent devices, switching devices, or control devices, there shall be one entrance to and egress from the required working space not less than 610 mm (24 in.) wide and 2.0 m (6? ft) high at each end of the working space.

A single entrance to and egress from the required working space shall be permitted where either of the conditions in 110.26(C)(2)(a) or (C)(2)(b) is met.

(a)
spacer.gif
Unobstructed Egress. Where the location permits a continuous and unobstructed way of egress travel, a single entrance to the working space shall be permitted.
(b)
spacer.gif
Extra Working Space. Where the depth of the working space is twice that required by 110.26(A)(1), a single entrance shall be permitted. It shall be located such that the distance from the equipment to the nearest edge of the entrance is not less than the minimum clear distance specified in Table 110.26(A)(1) for equipment operating at that voltage and in that condition.
 

Bwas

Member
Location
Florida
It is not the room that would, or would not, require two paths for egress. It is the working space that has that requirement.

Have you successfully made this argument with electrical inspectors? Can two paths of egress share a single door if near the equipment? If so, how far from the equipment does the door serving two egress paths have to be?
 