Just starting a small repair shop for electrical motors. Have a 3 phase 75 kva 120/208Y 480/277 step up transformer
Amp rating: 208/90
Have a 100A disconnect with 90A fuse in it.
Right now, I have a 200A Breaker on the primary side, I get a feeling its too small and I need to go with a 250A
Problem right now is, when I attempt to start a 75 HP motor, it trips the primary (200A) Breaker right away in the switch gear.
Does not blow the fuses on the secondary side (100A) Disconnect. I can start a 30HP motor up just fine. I'm getting the inrush current it too much for the 200A breaker?
Meg tested motor its good, no open, ground fault or short, has high resistance reading on all windings.
When energized, shaft tries to rotate then trips.
PM if you like