Full load is 75.4 amps so multiply by 125% gives me #1 thhn. (430.22) with #8 ground (250.122)
What about the conductors from the meter to the pump panel? The breaker is 100 amp at the pump panel...not sure about wire size from pump panel breaker to meter base. 430.24 says 125% of highest rated motor..but that is for a motor and other loads or several motors. This is just a pump panel supplying a motor, no other loads
This is an agricultural irrigation pump.
Thank you for your input.
What about the conductors from the meter to the pump panel? The breaker is 100 amp at the pump panel...not sure about wire size from pump panel breaker to meter base. 430.24 says 125% of highest rated motor..but that is for a motor and other loads or several motors. This is just a pump panel supplying a motor, no other loads
This is an agricultural irrigation pump.
Thank you for your input.