Hi I have a 2000 amp breaker at my facility it is being fed with 5 runs of 600 kcmil per phase
it is 480 volts. onthe load side of the breaker it has 6 spaces (lugs) per phase, i am only utilizing
5 as i said. Working under the tap rule could i land 1 more 600 kcmil on the breaker and run it
10 feet or less to a 400 amp fused dissconnect. When this new disconnect would be in use the
larger loads inside would not be.
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
Technically, yes, as Ron said.

Physically, it could be challenging to-get-her done with 10ft or less of cable. Better confirm your layout.

BTW: the fact that it is 2000A, load is not run concurrently or it is a 400A fused switch is inconsequential. At 2000A of current the protection will trip the breaker.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The 25 ft tap rule would require the "tap" conductors to have an amapcity of 1/3 the breaker rating
 