m c cable in damp locations

Status
Not open for further replies.

Bennetta

New member
Location
Louisiana
I cannot find in the 2011 NEC where m/c cable is not suitable for damp locations. I was advised the m/c cable would have to be stamped "suitable for damp location". I have researched and have not been able to locate a mfg that stamps the m/c cable for damp locations. They mfg for wet locations. Can you advise if m/c cable is suitable for damp locations and which article I need to research? Thanks
 

cowboyjwc

Moderator
Staff member
Location
Simi Valley, CA
330.10 uses permitted says (3)indoors or outdoors, but then you need to look at (11) which is wet locations. I would probably just have an issue with it since it will rust.
 