I would like some direction on MOCP-
Here is an example-
I have a 350ton chiller-480v 3ph
manufacturer data- 386 MCA, 301.8FLA, 600A MOCP
I understand the 600amp is the maximum overcurrent protection but don't I take the FLA- 301.8A x 125%= 377.25A which would allow me to use a 400amp fuse or breaker?
Thank you,