130617-1153 EDT
Dennis:
I was trying to get across the point that the main panel breaker was not protecting the motor. Something else has to do that, or the main panel breaker has to be designed to protect the motor and that is an unlikely situation as the original post was presented.
Thus, I tried to show that the motor was not protected by the main panel breaker by picking a load that would not likely stall the motor, but if no other protection was provided the motor would burn out.
.
The breaker protects the entire circuit, including the motor windings from short circuits and ground faults.
The motor overloads protect the entire circuit, including the motor windings from overload.