He mentioned capacitors reducing voltage drop so he must have meant a higher voltage at the motor terminals.How can I without knowing what you mean by "improved" voltage?
He mentioned capacitors reducing voltage drop so he must have meant a higher voltage at the motor terminals.How can I without knowing what you mean by "improved" voltage?
That's what I took it to mean. He also mentioned reduced current as an outcome.He mentioned capacitors reducing voltage drop so he must have meant a higher voltage at the motor terminals.
I agree that their wording is weird, and confuses things more than simplifies things.
I have been sizing caps a lot lately for individual motors, so I thought I would chip in. I go to the EC&M Elec. Calc Handbook for the equations and examples for doing these calcs. In one that I did, for a 100hp motor, the capacitor eliminated 17.82kVA of reactive power draw, which is about 21 Amps (FLA on the motor being 124A)
We know that real power is the power that does work in a system and reactive power contributes to the apparent power. If we can reduce the reactive power drawn from the utility, we will reduce the overall apparent power.
This article gives some good info that may help with understand how this works: http://ecmweb.com/power-quality/basics-pf-correction-single-induction-motors
This article also sheds a little more light on this: http://ecmweb.com/power-quality/troubleshooting-power-factor-correction-capacitors
The articles mention that harmonics decrease the power factor and detailed capacitor sizing to correct power factor. What they did not mention is that capacitors correct for displacement power factor caused by inductors, not the distortion power factor caused by harmonics.This article gives some good info that may help with understand how this works: http://ecmweb.com/power-quality/basics-pf-correction-single-induction-motors
This article also sheds a little more light on this: http://ecmweb.com/power-quality/troubleshooting-power-factor-correction-capacitors
Nor, as far as I can tell, did they mention any measures that need to be taken to prevent the capacitors taking excessive currents as a result of the harmonics that you typically see with a "dirty" supply.The articles mention that harmonics decrease the power factor and detailed capacitor sizing to correct power factor. What they did not mention is that capacitors correct for displacement power factor caused by inductors, not the distortion power factor caused by harmonics.
Ran across statements of capacitors cleaning up "dirty power" which they describe as a reactive power ripple. I would also like to discuss some of their other claims.
They mix a lot of fact with fiction. Some of the facts, at least for the commercial PACS product say that a capacitor should be installed near the reactive load. But then they go on to discuss huge savings and that power companies bill for kVA.
Another treat is reading about dirty power. Essentially they call reactive power the dirty power because it causes power ripples. I'm looking now for their take on harmonics.
Wrong, when an induction motor is taking full load: there is around 11% increase in full load current when the voltage is 90% of rated value per page no.36 ofMy point was that, if the voltage is low prior to adding PFC, that doesn't mean that it will necessarily take more current.
Here is a quote from the PACS's documentation:The sellers here dont say "power ripple" , they say "harmonics" and their power savers will take of harmonics.
yeah, right
They make the claim and get out. No elaboration.PACS helps to reduce one source of harmonics above 60Hz, which is present in the reactive power. All power lines contain many other frequencies. Reactive power is one cause of unwanted harmonics.
Nope. Not wrong.Wrong, when an induction motor is taking full load: there is around 11% increase in full load current when the voltage is 90% of rated value
You simply cannot generalise like that.
Reduced voltage at the motor terminals might make it take more current or less current.
Wrong, when an induction motor is taking full load: there is around 11% increase in full load current when the voltage is 90% of rated value
You simply cannot generalise like that.
Reduced voltage at the motor terminals might make it take more current or less current.
Nope.Bes:
What are you saying?
Are you saying the article of page 36 in my post #29 is wrong?
I don't doubt that one bit.Bes:
I will take infinite time..
Okay. Do you accept the application capacitor at motor terminals may serve to reduce the voltage drop along the motor circuit in case of low system fault level and motor running at full load ?you took the specific case of the motor running at rated load.
Perhaps you'd care to answer the question I posed in post #36 before we move on?Okay. Do you accept the application capacitor at motor terminals may serve to reduce the voltage drop along the motor circuit in case of low system fault level and motor running at full load ?
No OT please.Perhaps you'd care to answer the question I posed in post #36 before we move on?
If you don't want to or can't answer a perfectly straightforward question, that's fine.No OT please.