You're welcome- I have had maybe one or two complaints in all the years we have used TR. I use P&S and have been fortunate they don't appear to have a problem like some of the other manufacturers.Btw this is a gfi thx Dennis
I've had a few call backs because seniors are having trouble with them.You're welcome- I have had maybe one or two complaints in all the years we have used TR. I use P&S and have been fortunate they don't appear to have a problem like some of the other manufacturers.
I explained that you must plug in the device evenly and sometimes a little wiggle helps. Once they got it they were happy. People with arthritis have a much more difficult time with these then others
whats up w some of these new tr outlets
customers cant even get their plugs in
any tips to give them like
rock it back and forth :/
I too have had trouble with Leviton TR GFCI's. Such testimony is only anecdotal evidence that one brand is worse or better.New Leviton slim ones
My neighbour, who is older and has early Parkinson's, did a new addition. TR recpts had to be installed. He had a lot of trouble with them.So what am I supposed to tell them?
To wiggle it or that I replace it for free =0
How do members feel about the customer using a UL-listed multiple tap duplex receptacle plug-in for a situation like this? The receptacle is still TR and no modifications have been made to the building wiring. If there is a concern about too many appliances plugged in, just insert or glue baby guards into 4 of the 6 receptacles.I too have had trouble with Leviton TR GFCI's. Such testimony is only anecdotal evidence that one brand is worse or better.
My neighbour, who is older and has early Parkinson's, did a new addition. TR recpts had to be installed. He had a lot of trouble with them.
Weeks on down the road he invited some guests over for a really good dinner. One of those guests had the tools and parts to retrofit the TR recpts with non-TR.
If I provide a TR receptacle I have met code. I can't control what gets plugged into a receptacle later on.How do members feel about the customer using a UL-listed multiple tap duplex receptacle plug-in for a situation like this? The receptacle is still TR and no modifications have been made to the building wiring. If there is a concern about too many appliances plugged in, just insert or glue baby guards into 4 of the 6 receptacles.