630.11[B]
m sleem
Top-notch Сasual Dating - Real-life Females
Usa
Health
Can we use that section to calculate the demand?
petersonra
Northern illinois
engineer
It appears that this section on its face only applies to determining conductor ampacity.
Presumably by "demand" you are actually asking about a load calculation. Those are covered in article 220. It refers you to 630.11 and 630.31. However neither of those sections says much about load calculations only about ampacity of conductors.
So I don't know what that means.
david luchini
Connecticut
Engineer
That is similar to determining motor loads. 220.14(C) tells you that the load for a (single) motor should be calculated in accordance with 430.22. 430.22 doesn't really say anything about load calculations, only about ampacity of conductors.
petersonra
Northern illinois
engineer
I never really noticed that before. A strange way of specifying loads.
m sleem
Usa
Health
That is similar to 517.73(2). Since those sections indicates the required cable ampacity so 215.2(A)(1) is not applicable.
Beside that which ampacity is meant here (before or after correction)?