HI all!!
The town I work for has renovated the fire station and installed a nice 600A service. The issue I am having is the engineer required a 4/0 GEC between the POCO pad mount and the main switch. The 4/0 is not in the conduits with the service entrance conductors but does bond to the UFFER and the communications tower.
I'm calling this a paralled neutral and am wanting to see it disconnected at the POCO transformer.
What say you??
Thanks
Paul
The town I work for has renovated the fire station and installed a nice 600A service. The issue I am having is the engineer required a 4/0 GEC between the POCO pad mount and the main switch. The 4/0 is not in the conduits with the service entrance conductors but does bond to the UFFER and the communications tower.