I am installing a manual transfer switch and a hook up for a 400amp temporary generator. I have run parallel 2" EMT conduits with 3/0 to the location were the generator will sit. Here is the question.... Do both pipes need bonding bushings on all connectors going back to the manual transfer switch? The generator that is powering up the system has a main breaker in it.... so the way I look at the scenario is that is the first system disconnecting means is that main breaker on the generator so the pipes doe not need to be bonded.... Is this correct?