Damn, the rest of us have been running raceways without considering if the conductors would fit. :D.

Well, I may have overstated the obvious when it comes to more cable than you have raceway for, but even when following the 40% fill rules for power conductors, I have had plenty of 40% or less filled raceways that have pulled pretty hard. So I would think if I had similar fill with communications I still would not want more than 40% fill on a long pull or one with three or four 90 deg bends
 

twoelk

Member
Location
USA, West Coast
If you go to the Belden web site, you should be able to get a free slide calculator sent to you. It have lots of cables on it, with diameters, and tells you how many will fit in conduits
 