As I look at this example problem in Annex D3 I come across a note at the end:
In the example, 125% of the actual connected lighting load (8500 VA x 1.25 = 10,625 VA) is less than 125% of the load from Table 220.12, so the minimum lighting load from Table 220.12 is used in the calculation. Had the actual lighting load been greater than the value calculated from Table 220.12, 125% of the actual connected lighting load would have been used.
Looking at the example itself you would see that the 125% factor is not applied to the continuous load as per Table 220.12 and is subsequently added to the noncontinuous load. But Mike Holt and James Stallcup both say that the 125% factor is applied regardless of whether the actual connected load or the Table 220.12 calculation is greater. Does anyone care to comment on this?
In the example, 125% of the actual connected lighting load (8500 VA x 1.25 = 10,625 VA) is less than 125% of the load from Table 220.12, so the minimum lighting load from Table 220.12 is used in the calculation. Had the actual lighting load been greater than the value calculated from Table 220.12, 125% of the actual connected lighting load would have been used.
Looking at the example itself you would see that the 125% factor is not applied to the continuous load as per Table 220.12 and is subsequently added to the noncontinuous load. But Mike Holt and James Stallcup both say that the 125% factor is applied regardless of whether the actual connected load or the Table 220.12 calculation is greater. Does anyone care to comment on this?