I like to ask you guys your opinun on the use of large al cable [400] being spliced underground using a copresson connection. What is the best method to seal the connection with since the wire will be in water @ times ? We have used the 3m splice cover , doesnt seem like enough protection . Does anyone use something better thats going to last ?
The cables had a couple of burn out spots and we made repairs to them.
Thanks for the time dealing with my questions.
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
We use compression butt splices and Epco heat shrinks most of the time. Occasionally we use a gel filled one that wraps around the splice, snaps together and is secured with cable ties. We have not had a call back on those yet but they are fairly new. IMO the ones that have the plugs you insert into them after tightening a setscrew butt splice a POS. They leak and I have replaced way to many of them...including.

I have had very limited experience with the cold shrinks.
 

kwired

Electron manager
Location
NE Nebraska
Never seen heat shrink fail, have seen other methods fail. It needs to be heat shrink with a sealant added, which all that are rated for underground use have AKAIK.
 