Hi guys. This is something I came across in a home I was doing some work in:
-Meter pedestal with 100A breaker located on exterior of home
-GEC connected to grounded conductor at pedestal. One ground rod installed
-SE cable (3 conductor) from pedestal feeds panel inside house
-Galvanized water piping connected to neutral bus in interior branch circuit panel with #6 solid
My question is isn't the connection of the galvanized water piping to the neutral bus in the panel creating a parallel path for neutral current?
The homeowner says this was installed 20+ years ago. My guess is that the installer was using the water piping as an additional grounding electrode seeing as there is only one rod outside (at least that I can see)