Bonding Bushing for Feeder (SER)

Status
Not open for further replies.

euclid43

Senior Member
I am using SER #1 aluminum to feed a subpanel; do I need a bonding bushing when connector clamps are used at both ends (consentric KO). I wouldn't think so.
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
No BB on the SER cable.

Don't even need a bonding bushing on the concentric or eccentric knock outs, unless if the voltage is higher than 250V. even the 250V requirement has exceptions to it.
 
Last edited:

aftershock

Senior Member
Location
Memphis, TN
Sorry if there was any confusion. I used the term "fiber bushing" loosely.
We must have some type of bushing whether it be plastic, fiber or metal on any connector larger than 1/2" even if the connector is PVC.
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Local codes here require a fiber bushing on any connector larger than 1/2". Wire size does not matter

I would love to see the amendment requiring that.

Around here, there is a lot of confusion on this issue, and the NEC rule is surprisingly simple for all the confusion. I hear bushings are required under a bunch of different conditions that I don't believe were ever in the NEC.
 

aftershock

Senior Member
Location
Memphis, TN
I would love to see the amendment requiring that.

I would love to see it too. I can only go by what I have learned by getting turned down for something the inspector says is a local requirement. I have tried to acquire some type of documentation listing all the local codes. Sadly either there is none or I have yet to find the right person to ask. I have some documentation from the mid 80's and we do sometimes get amendments sent to use but a lot of the times we find out what they are when we get turned down for something.
One example which is not very good.
An 8' ground rod is suppose to be 8' in the ground. (Don't have my code book handy so I do not know the correct wording)
In Bartlett, Arlington and Collierville which are in Shelby county, but have their own inspection offices, the ground rod must be 8' in the ground and have a clamp listed for direct burial.
In all other areas of Shelby county, the ground rod must be exposed above the ground with the clamp accessible.
 

TobyD

Senior Member
So if I was to use 1" NM connector with a locknut I would have to use a bushing?

That makes no sense to me and like George would like to see the amendment wording.:)

I think that the application is only on // conduit fittings with exposed threaded(connectors --adapters) ends.As far as Tn.ammendments I don't think it applies to NM type or SER. cable
 