Commercial Kitchen GFCI's

Status
Not open for further replies.

Nietz001

Member
Location
St Paul MN
Is it ever acceptable to install a 120v rec in a commercial kitchen that is not GFCI protected? I was told if the equipment (such as a refridgerator) is difficult to move or fixed in place it's OK to make it a single rec and no GFCI? Just doesn't seem right, looking for help.
 

iwire

Moderator
Staff member
Location
Massachusetts
No there are no NEC exceptions for 15 & 20 amp, 125 volt receptacles in a commercial kitchen. Regardless of how hard they are to access they must be on a GFCI.


There used to be exceptions for GFCIs in dwelling unit basement and garages for dedicated appliance outlets and some folks thought they applied to all GFCIs .... they did not.

Now those exceptions are gone anyway.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Also the GFCI has to be readily accessible for testing purposes. That means a remote device or a GFCI breaker if the equipment cannot be moved.
 

kwired

Electron manager
Location
NE Nebraska
Is it ever acceptable to install a 120v rec in a commercial kitchen that is not GFCI protected? I was told if the equipment (such as a refridgerator) is difficult to move or fixed in place it's OK to make it a single rec and no GFCI? Just doesn't seem right, looking for help.

I think the original proposal to include all 120 volt commercial kitchen receptacles was prompted in part by an electrocution involving a refrigerator and a bad/missing equipment grounding conductor IIRC.
 
Is it ever acceptable to install a 120v rec in a commercial kitchen that is not GFCI protected? I was told if the equipment (such as a refridgerator) is difficult to move or fixed in place it's OK to make it a single rec and no GFCI? Just doesn't seem right, looking for help.

Another thing to note is that most commercial kitchens have to deal with a health departmental authority. Alot of them require that food in freezers, refrigerators etc... be monitored. So if the power went off and the temp started to drop, the alarm should go off and one can save the food.
 

kwired

Electron manager
Location
NE Nebraska
Another thing to note is that most commercial kitchens have to deal with a health departmental authority. Alot of them require that food in freezers, refrigerators etc... be monitored. So if the power went off and the temp started to drop, the alarm should go off and one can save the food.

Dropping temp or rising temp?;)
 

kwired

Electron manager
Location
NE Nebraska
I'd love in invest in that. I got $20 that's just burning a hole in my pocket.:D