Hi,
I need some help with a project that im working on. Its a 3 phase 480V 4 wire main. I am using 8 qty 20 kW inverters. Output current comes out to 27.3 Amps per phase, per inverter. Can some please let me know if I am doing this correctly??
27.3 A x 1.56 = 42.58 A, so I am using 50A 3 phase PV breaker per inverter in my load center/sub panel.
from my sub panel/load center to the ac disconnect and main service panel I am using:
42.58 A x 8 inverters = 340.7 A, so I am using 350A 3 phase PV breaker and 350A fuses in my AC Disconnect.
my wires calcs from my sub panel to my ac disco and main panel are:
340.7A / .87 / .8 = 489.51A = 700 kcmil where i will use 750 kcmil to accomodate Voltage drop.
Can someone please confirm. I would really appreciate it. Thanks hope to hear back from someone.