JoeStillman
Senior Member
- Location
- West Chester, PA
mgphill recently posted a question about sizing conductors. He's an EE student with a pretty good grasp of the concepts in the NEC. My hat is off to him for not being led astray by references he has found to a "demand factor" of 125%. The 125% multiplier in chapter 2 of the NEC is not a demand factor. Demand factors are always less than 1. (See the definition of "demand" in article 100.)
So if the 125% factor we all know and love is not a "demand factor", what is it? It is similar to the derating factors of Table 310.15(B)(2)(a)-"Adjustment Factors for More Than Three Current-Carrying Conductors in a Raceway or Cable". Now that's a mouthfull. Most people refer to these as the "derating factors", although that term is used elswhere for something a little different (310.60) and not included in the definitions.
If all the derating factors are less than 1, then our 125% factor can't really be a "derating factor." It's really the reciprocal of a derating factor, so I propose we call it the "Rating Factor". All in favor of calling it the "Conductor Rating Factor" raise your hands.
Now if we could only get the NFPA to include it in article 100....
So if the 125% factor we all know and love is not a "demand factor", what is it? It is similar to the derating factors of Table 310.15(B)(2)(a)-"Adjustment Factors for More Than Three Current-Carrying Conductors in a Raceway or Cable". Now that's a mouthfull. Most people refer to these as the "derating factors", although that term is used elswhere for something a little different (310.60) and not included in the definitions.
If all the derating factors are less than 1, then our 125% factor can't really be a "derating factor." It's really the reciprocal of a derating factor, so I propose we call it the "Rating Factor". All in favor of calling it the "Conductor Rating Factor" raise your hands.
Now if we could only get the NFPA to include it in article 100....