I am installing a step down transformer 75 KVA in order to get a neutral
primary: delta 240 Volts - secondary: why 208Y120 Volts
to my calculation I need 180 Amps for line side 75,000 / 415 (240 X 1.732 = 415) And 208 Amps for load side 75,000 / 360 (208 X 1.732 = 360)
I just wonder if that's correct
because when i checked out the transformer the line side lugs where a lot smaller then the load side and the same is for the internal wires of the line side?
thanks
primary: delta 240 Volts - secondary: why 208Y120 Volts
to my calculation I need 180 Amps for line side 75,000 / 415 (240 X 1.732 = 415) And 208 Amps for load side 75,000 / 360 (208 X 1.732 = 360)
I just wonder if that's correct
because when i checked out the transformer the line side lugs where a lot smaller then the load side and the same is for the internal wires of the line side?
thanks