240 volt service without neutral

Status
Not open for further replies.
I am installing a step down transformer 75 KVA in order to get a neutral
primary: delta 240 Volts - secondary: why 208Y120 Volts
to my calculation I need 180 Amps for line side 75,000 / 415 (240 X 1.732 = 415) And 208 Amps for load side 75,000 / 360 (208 X 1.732 = 360)
I just wonder if that's correct
because when i checked out the transformer the line side lugs where a lot smaller then the load side and the same is for the internal wires of the line side?

thanks
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Your calculations are correct, of course, the size of your overcurrent device will also be prevalent in determining wire sizes. { Note the last sentence in 240.21(C) }

If I observed the lug and wire sizes you note, I would double-check to assure I did not accidentally received a transformer with a 480 primary since they are by far more common.
 
If I observed the lug and wire sizes you note, I would double-check to assure I did not accidentally received a transformer with a 480 primary since they are by far more common.

yes I did and its the right transformer, I didn't check what size the lug is but the they are by far to small for 3/0 or 4/0 wire, should i just change them out?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
I was under the impression that most 75kVA transfromers were sold without fatory installed lugs.
 

kwired

Electron manager
Location
NE Nebraska
Usually the lugs are field installed, but in this case maybe an assembly mistake - they likely assemble many more that are 480 volt primary and just installed the usual components?
 