I want to change the service to a 6 unit apartment building. In Chicago. The load calculation came to a 400 amp, 240 volt, 1 phase service. 6 dwellings and a public panel. I believe the 310.15 (B) (6) table applies to each of the apartments 100 amp feeders. Meaning #4 CU, in 1" pipe. The question is does that section and table apply to the service riser? Meaning the from the weather head to the main disconnect and from the main disconnect to the meter bank? My guess would be no, but I'm not sure. The table would allow 500 KCmil in 4" IMC, outside to the main disconnect and 4" EMT inside from the disconnect to the meter bank. If I can't use 310.15 (B) (6) then I have to use 310.16. That requires 600 KCmil, in 3 1/2 IMC and EMT.
Thanks
Mike
Thanks
Mike