Where to bond

Status
Not open for further replies.

sketchy

Senior Member
Location
MN
Our company installs wind turbines that put put out 480 volts, some single phase some three. On the single phase units, I need to usually feed back to the home owner. To do this we use a single phase 480 - 120/240 transformer with a fused disconnect on either side. IMAG0079.jpg
I have been bonding the 240 volt disconnect with the supplied bonding screw and not bonding the case of the transformer or the 480 side. So I have 2 hots, a neutral and a ground from the 240 volt disconnect where it is bonded, terminate on the X side, then from the H side I have 2 hots and a ground going to the next disconnect. The grounds in the transformer terminate on a lug mounted to the case. This is acceptable isn't it? The turbine doesn't need a neutral.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I was in hopes you didn't ask :D
I'm still trying to grasp the changes tp 250.30 in the '11 Code.
I may be wrong but you may still install the system bonding jumper at the source or 1st disconnecting means. Note that 250.30(2) does require a supply side bonding condcutor between the two.
This, I think, is still permissible:
transformer.jpg
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
I think Augie is telling correctly for the 120/240 side, but I'm wondering about the 480 supply side. This needs to be a grounded system to be safe and compliant.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Is there a grounded conductor on the 480 volt side? If not you will need a ground detector on the 480 volt side. 250.21(B)
 

sketchy

Senior Member
Location
MN
How is this any different than a 240 v circuit with two hots and a ground? No need for a ground detector then.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
How is this any different than a 240 v circuit with two hots and a ground? No need for a ground detector then.

A 240 volt circuit with 2 ungrounded conductors and a EGC are fed from a grounded system, that is the difference. I think what we are thinking here is that your 480 volt source is operating as an ungrounded source, and would not have a fault return path. Even with no neutral you can still create a grounded system.
 

sketchy

Senior Member
Location
MN
Well I would love to hear any ideas on how to create that without a neutral. Never heard of single phase 480 until I started working here and the more I find out the more I wish I never heard of it.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
How is this any different than a 240 v circuit with two hots and a ground? No need for a ground detector then.
Most 240 volt transformers that have a center tap and would be required to be a grounded system by 250.20(B)(1). If the 240 volt transformer has no provisions for a center tap, then it would need a ground detector.
You could ground one of the 480 volt legs, making that a grounded system and then a ground detector would not be required.
 

sketchy

Senior Member
Location
MN
I am bonding X2-X3 (neutral) to ground in the disconnect. We have only done 2 of these and they both passed inspection.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I am bonding X2-X3 (neutral) to ground in the disconnect. We have only done 2 of these and they both passed inspection.
That makes the 240 side a grounded system and you would not need ground detectors. The 480 volt side is an ungrouned system and will require ground detectors.
 

tom baker

First Chief Moderator
Staff member
How is this any different than a 240 v circuit with two hots and a ground? No need for a ground detector then.

The difference is its 480V to ground. 240 is almost always 120 V to ground. A 480 volt ground fault is very dangerous and will not burn clear as will a 120 V ground fault
And if you have 480 volt and get a line to case ground, you have just created a grounded 480 V system. Your second line to case fault will be a line to line short circuit at 480 V.

What I suggest you do is start with 250.20 and determine what systems must be grounded, what systems are optionally grounded and what systems are never grounded.
And then look at the requirements for operating ungrounded sytems
 

sketchy

Senior Member
Location
MN
Can you just create one, neutral or grounded conductor, by tying H2 & H3 together and grounding the mid point on the primary side? IDK. Open ended question.

I have thought of that as well, not sure it's leagal. The transformer nameplate lists only single voltages on the H side, where as the L side lists 120/240.
 