thanks
breaker cost is not an issue.
Most of the transformers I deal with are delta tri-delta with phase shifted secondary that feed a single VFD and 1500hp+ motor.
Great. But may one consider the 480v or 277v to ground issue? Motor failure, when a winding fails and goes to ground, what voltage would you prefer should there be an arcing fault? What voltage would be kinder on the phase to ground insultation resistance? Which one may do less damage should there be a winding failure?
If you did have a choice which direction would be the best?
The 1500hp more may not likely be 480v but 2300v are possibly 4160. But the phase shifted secondary may not even be an issue unless it relates to another transformer secondary voltage.
Now that you brought up having a delta consisting of (3) 1ph transformers it may have an advantage of being able to continue to supply the load should 1 transformer in the back goes south. But the remaining (2) transformers must be of a suitable size to suppy the load. Otherwise a singe 3ph transformer with a delta secondary does have much to bring to the party over a transformer with a wye secondary in my opinion.