Additional disconnects required?

Status
Not open for further replies.

kbsparky

Senior Member
Location
Delmarva, USA
702.11 was 2008 the same for 2011 is 702.12...

No argument here. 702.11 has to do with grounding and bonding of portable units, which is not applicable. 702.12 has to do with outdoor generator units, and is applicable here.

The question that has been raised is whether the built-in disconnect is "suitable for use as service equipment" or not. Usually, this means that the disconnecting means can be configured for the neutral to be bonded to the ground to earn such a rating. I'm not sure about whether the unit qualifies to meet this requirement, this is something that needs to be investigated.

But then the question comes to mind IF an outside disconnect is required to be "suitable for use as service equipment" BUT since it's controlling a FEEDER which can NOT have its neutral bonded again, isn't this a conflict of requirements?

...As long as the transfer switch has a UL 1008 it would be compliant

I did manage to discover that the transfer switch is UL 1008 listed.
 

kwired

Electron manager
Location
NE Nebraska
My house is like that, with a disconnect on the house, 25 feet away from a garage with no additional disconnect in there.

Like you said, it's "outside" and "within sight" of the garage, and the AHJ did not require anything further.

So if there is qualifying grounding electrodes present at the garage you would have to run the GEC to the disconnect on the house, not saying it can't be done. Not all AHJ are going to accept the disconnect 25 feet away on another structure.
There is no clear language that I am aware of stating that "within sight" is acceptable or for that matter not acceptable for this circumstance.
 