It has been a common practice to run two sets of underground wire from the POCO transformer to a house that required a 400 amp service. These two sets were the service entrance conductors for two - two hundred amp panels with the main breakers serving as two service disconnects. These panels are located side by side (grouped). The two sets of service entrance conductors do not connect to each other after they leave the transformer. I am now being told that the two sets of service entrance conductors have to terminate in 400A rated equipment first and then have as many as six disconnects. (not sure what this means yet) I am guessing that the inspector is requiring a 400A disconnecting means or a junction box or a terminal box.
I assumed that the exception #2 to 230.40 covered this.
Exception No. 2: Where two to six service disconnecting
means in separate enclosures are grouped at one location
and supply separate loads from one service drop, set of
overhead service conductors, set of underground service
conductors, or service lateral, one set of service-entrance
conductors shall be permitted to supply each or several such
service equipment enclosures.
I am being told that this only applies to separate occupancies ( strip malls etc.)
Any thoughts ??
I assumed that the exception #2 to 230.40 covered this.
Exception No. 2: Where two to six service disconnecting
means in separate enclosures are grouped at one location
and supply separate loads from one service drop, set of
overhead service conductors, set of underground service
conductors, or service lateral, one set of service-entrance
conductors shall be permitted to supply each or several such
service equipment enclosures.
I am being told that this only applies to separate occupancies ( strip malls etc.)
Any thoughts ??