motor calculation

Status
Not open for further replies.

RonR

Member
I need to run a 40 hp and a 30 hp motor at the same time.

I will be feeding both motors from a step up xfmr(208/120v 3 phase to 480 v 3 phase)
to a panel that has a 175 amp main breaker. What is the required Kw rating of the step up xfmr??


the existing step up xfmr is 112.5 Kw and it is running a 20 hp and a 30 hp at
the same time.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I need to run a 40 hp and a 30 hp motor at the same time.

I will be feeding both motors from a step up xfmr(208/120v 3 phase to 480 v 3 phase)
to a panel that has a 175 amp main breaker. What is the required Kw rating of the step up xfmr??


the existing step up xfmr is 112.5 Kw and it is running a 20 hp and a 30 hp at
the same time.

You are around 75 kVA with both motors running. 112.5 is probably adequate.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
So in the end you have a 112.5kw trany that will run a 40 hp, 2- 30 hp and a 20 hp motor? I think you will be okay
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The breaker depending on the wire size to the transformer could be fine. I expect that you have a panel with a breaker on the load side of the trany?
 