Trouble call was reported as Motor Operated Gate stopped working.... This is what I found. :)

photo-12.jpg


photo-9.jpg


photo-8.jpg


photo-11.jpg


photo-10.jpg


This is what happens when you use AL. split bolts in wet locations, and by the way, there were about 6 of these in ground junction boxes with no drainage provisions...
 

kenaslan

Senior Member
Location
Billings MT
Cha-Ching Other peoples stupidy makes for a fat check.

Reminds me of the other day I inspected an installation. I spec 4/0 awg for a 225 amp feed. The contractor installed 4/0 AL. When questioned he responded that AWG meant Aluminum Wire Gage. What is worse is that the city inspector signed off on it
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
Cha-Ching Other peoples stupidy makes for a fat check.

Reminds me of the other day I inspected an installation. I spec 4/0 awg for a 225 amp feed. The contractor installed 4/0 AL. When questioned he responded that AWG meant Aluminum Wire Gage. What is worse is that the city inspector signed off on it

That's a good one.:slaphead:
 

Hendrix

Senior Member
Location
New England
Cha-Ching Other peoples stupidy makes for a fat check.

Reminds me of the other day I inspected an installation. I spec 4/0 awg for a 225 amp feed. The contractor installed 4/0 AL. When questioned he responded that AWG meant Aluminum Wire Gage. What is worse is that the city inspector signed off on it
Then CWG is copper wire gage:?
 