I just check the UL book and there is no mention of plenum rated LFMC
That is under raised floors-- not what we were discussing. Doesn't mention the floor as a plenum eitherDennis, what about 645.5(D)(2)
That is under raised floors-- not what we were discussing. Doesn't mention the floor as a plenum either
Drop down to condition (4) and it will references 645.4.(2) the HVACR system serving the raised floor.
Gregg we are not talking about a raised floor.Now look at 300.22(2)(D)
Gregg we are not talking about a raised floor.
The OP is clearly asking about a raised floor in a computer room with air in the floor, which is an air handling space and Article 645 applies and allows LFMC
I am totally sorry, One sentence long & I missed it and couldn't understand why you kept bringing it up. Mea Cupa....:ashamed1: